What is transformer tap changers please explain
Answer Posted / byd
i am working at Transformer factory as test engineer, tap
changer is the part of transformer's primary winding which
is use to balance secondary voltage, for example we
have transformer which feature are: 630kva, 33/0,400 kv,
and this transformer has a tap changer , transformer
primary voltage positions are like these
HV(v) Lv (v)
28500
30000
31500
33000 ....... 400 v
34500
36000
network voltage is 33000v but sometimes it can be
increase or decrease , you can change tap changer:)
but this for no-load tap changer for distrubition
ransformer, if it is power transformer you should use
load tap changer
| Is This Answer Correct ? | 9 Yes | 3 No |
Post New Answer View All Answers
wheather the size of windings in motor and generator are the same
How much kv gas generator is needed to run 2 hp and 1 hp airconditioners, plus a refrigerator and 4 Tvs
why on delay timer used for fully automatic star delta starter?
what is thermal resistance of PVC Cable.
Who are the manufacturer for Nitrogen based Fire Protectio/explosion prevention for Oil Filled Transformers? India and international both?
What is force on parallel conductors ?
if a 3phase 100kva distribution transformer , 400 v,50 hz, 4-wire system is loaded at 160 k.w mostly 1-phase Lighting & Airconditioning split a.c load what will be the net effect on the power system in terms of voltage, powerfactor, current , efficiency of xformer
i have completed deee and i've (June2012-feb 2015 experience in electrical maintenance in pvt ltd company.company having HT & LT electrical power.how to apply electrical C-license ,NOW I was resigned my job,what are requirements of applying for c-license
What is the difference between type1 and type2 relay protection co-ordination for motor feeders
clarify types of motor operated valves and advantages
What are the basic & Majour problems in UPS ?
What is the drawback of static coefficients?
What is the slip speed?
PLEASE INFORM ABOUT THE IDEAL TEST RESULTS OF MAGNETIC BALANCE TEST OF TRANSFORMER 33/11 kv DELTA-STAR T/F
How to size Air Circuit breaker (ACB)? What is the most important factors?