Answer Posted / arpit sood

one of the reason according to me should be that a motor
with star connection draws less starting current (5-8 times
less)
so if the motor is HV then there will be less voltage
fluctuation and less heating of the insulation of the motor
at starting
so the motor is better protected and does not start with a jerk


but generally the large motors are designed for delta
connection due to more mechanical power ( 3 times more than
the star connected) so there is need of auto transformer
starting

Is This Answer Correct ?    2 Yes 7 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is meant by the phrase 'static load' in case of shorting in a generator excitation system?

1714


Why there are some equipment(i.e:TV) that using 2-pin plug instead of three? What happen if there is current leakage? Are we going to get electric shock??

1730


I have a CT meter with ratio 60/5. The meter reading of previous month was 3290.49 and that of current month was 3797.26. How many chargeable units as per normal meter should be my reading.

984


1.what is meaning of curve into a mcb. 2.what is basic reason changing of curve

1548


what is the use of permanent magnet generator in exciter

1703






why constant voltage transformer should be start without load? and if started then what will happen?

1618


Hoe do calculate the Cable size for Amps rating ?

1694


Dear friends I want to design busbar for1600 kva transformer(i.e2100 amps) what are all the factors to be considered before selectinga busbar what are all the standard sizes of busbars what is the formula for finding current of copper and aluminium busbar

1488


how to calculation increase capacitor,increase power factor for three phase.

1640


What is Antipumping Function & If we have C.T how we find the Ratio ?

1529


How can we measure the residual voltage in dc machines?

1223


How can we connect additional batteries to three phase ups? What are parameters we have to check when connecting?

1512


when generator short circuit condition, the current how dissipates. or at short circuit voltage not available then current how can flow?

1758


what parameters are should nessary for control technic dc drive(in rolling mills)?

1518


List of equipments required foe industrial repair lab.

1513