1.what is difference between line,neutral and earth
2.IF single phase voltage is 230v ac and what should be the
voltage between line to neutral,neutral to earth and earth to
line
Answer Posted / k.prakashchandra
The star point of 3 phase supply is the neutral.The phase
wires are lines.The voltage between line and neutral is 230
V so also between line and earth if nrutral is earthed.The
voltage berween N and E is zero.
Is This Answer Correct ? | 9 Yes | 1 No |
Post New Answer View All Answers
What current flows in the transformer primary when its secondary is open?
what the Microsoft .NET framework is?
Differentiate between low pass, high pass and band pass filter?
What is ramp signal?
why normally Generator rating are between 11Kv to 22Kv?
what is load despatching
What willbe change in programming when we use 5/3 solenoid inplace of 5/2 in operating of a cylinder?
What is the Load Capacity of Panther conductor (0.2) and dog conductor (0.2)
What are the factor to be consider for CT selection in 132kV substation?
how to prepare the technical test
When calculating the speed of a rotor required for a particular frequency of synchronous generator we use the equation 60f/p Is this p is the number of pole pairs of rotor & do we consider the number of pole pairs in the stator is 1?
What is touch potential and step potential?
Draw a circuit diagram in which if button is open we can use socket and bulb as a series test circit and if button is close than simple we can use socket as any load purpose.
how many load we can take for lighting
if two transformers are placed parallel & both have fault impedance of 50KA will it increase or decrease show example?