how to calculate earth resistat in earthpit with earth
testing kit?

Answer Posted / thanigaivel

In that earth tester E1 and P1 short with wire and take a lead from that loop. and put 2 spike in that mother earth 1st spike connected to E2 and p2 connected to that another spike ... that looped wire is connected to earth bit . and put the earth test with ohms .. its show the value

Is This Answer Correct ?    4 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Can any answer me ,What will be the range of C.T coil for L&T energy meter EM301 used for 180 kva DG set

1941


Is potential difference materials property ..? if yes tnen how.. explain brifly.

1775


What is the type of earth fault protection used in battery? explain.

2038


In siemens PLC, why do we want to move the data ?

2058


How we can come to know the substation range,without go through any name plate ?

1744






How to know about the rating(voltage and other) of induction motor if its name plate is missing at the manufacturing site.

3074


According to IEC60034-14, When the vibration monitoring system required for motor Bearing. above which KW, it is required? and for what type of bearing the vibration probe is provided.

3920


EXPLAIN THE WORKING OF SERIES REACTOR IN HT CAPACITOR BANKS (FOR VOLTAGES & CURRENTS)

7872


How many types of losses occur in a transformer?

894


Its possible to use 3core 2R of 240 sq.mm cable for 3phases & separely 50sq.mm 3core cable fully for Neutral for connection of PCC to MCC 3ph..4wire system?

1872


What will be advantage if we put some load in neutral of grounded star transformer & loadshortcircuit current,rated current of cable & MCB with example?

1598


is there any role of power factor with frequency variation? and how we can manage the frequency variation?

1806


How to calculate cable size by using load.?? Any formula...

1068


What is George phenomena to start the synchronus machine?

3840


state the working of discharge lamp?

1763