What is the working of AVR in AC generators?
Answer Posted / raul
AVR- AUTOMATIC VOLTAGE REGULATOR
AVR is a device used to measure any difference in the
generator terminal voltage and highly stabilized reference
value, and if it detects any difference, it controls the
firing pulses of the thyristors connected in the
system.....to change the output voltage of the pilot
exciter which in turn changes the output of the main
exciter n ultimately the generator voltage........
IN SHORT, IT IS USED TO MAINTAIN THE GNEREATOR TERMINAL
VOLTAGE B/W THE TRANSIENT STABILITY LIMITS so that d
generator remains in synchronism
| Is This Answer Correct ? | 17 Yes | 2 No |
Post New Answer View All Answers
Why Ac Systems Are Preferred Over Dc Systems?
what is the effect of un-synchronized power.
What is the different types of cable & current capacity of cable
CPC cable .PVC \1C....I want to get sure that type is flexible indoor or to be install on trench. please advice .thanx :)
how is the cable tray designed & how its total length is calculated for an Industrial plant Say for Ex. (500KW Motor Load)
what is a speed of rotor when we give supply to stator of 50hz and as well as rotor of 60hz of an induction motor?????
What is the loss of transformer of 220kv/11kv, 63/80 MVA and 18.05% impedance
how we arrange the hv side with delta connection in case 33/11kv of transformer.
Define sensitivity?
What is Antipumping Function & If we have C.T how we find the Ratio ?
In Plumbing services What are accessories we consider for a bathroom?
what is the acceptable limit value for Desolve Gas Analysis/
Which capacitor is preferred for high voltage and frequency?
what is different between phase and netural
If symmetrical fault occurs at the terminal of a synchronous motor then how the motor will act...explain it..