how do i calibrate mmwc pressure guage with out
calibrator.if any? pls give me the ans.
Answer Posted / ashraf
You need one water manometer,one T fitting and one flexible
rubber hose. Connect the hose,the manometer and the pressure
gauge to the T fitting without any leakage.
Blow air (by mouth)through hose till span (cross check at
water manometer) and fold the rubber hose. Adjust span setting.
Then drop the pressure by unfolding the hose and adjust for
zero.
Repeat process two or three times.
Now check for mid-range, if it is ok, then calibration is over.
| Is This Answer Correct ? | 9 Yes | 1 No |
Post New Answer View All Answers
What is the diffrence between digital signal processing and discrete signal processing?
What is the differerence between hysterisis and linearity.
steps for installing orifice plate?
in mass flow meter what is drive friquancy ?
How r the calculation of process line mpm.
Instrument QA/Qc what is the project quality plan?conduit inspection RFI. which documents attache with package?
What is compensation for flow ? Why we use compensation ? What are the factors of different compensation ? We not use then what problems may happen ?
applications of plc in printing and packaging?
IS there any effect of vortex in low pressure side of the transmiter after the orific in feed water line? if yes then what is the calculation?
when the instrument tapping on pipe line is located below and transmitter is located above the tapping point for liquid service transmitter, what should we do, is there any additional drain valve is required??
Name different parts of a pressure gauge.
can u plz send me technical questions asked in SCHNEIDER ELECTRICAL technical paper?
How to find out the current of two motors having same power consumption but different RPM?
protection relay watchdog contact operation?
why we r opening HOT BYPASS valve during startup of a compressor?