Who is reputed manufacturer of TNC switch for ACB in India ?
Answer Posted / k.prakashchandra
Recom,Mumbai and Switron,Nasik.It may be ACB or something
else, ask for control switches for CBs with current rating.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
How harmonic block test are conducted on relays ( Siemens,Areva ect )power transformer using omicron kit?
if we give 60 hz single phase supply to the transformer used in europe , than what will happen
What is the tests required for a 132 kV, 400 kV , 765 kV for a Circuit Breaker and Power Transformer before commissioning ?
Explain difference between stand by earth fault and residual earth fault protection?
What are gain margin and phase margin?
why we have to particulary use ACB for below ratings,even available of MCB,MCCB with that range ?
Parts of machine and their discription in details with suitable photo
what should be correct gas pressures to be a 1.5 ac unite
What is the safety of UPS?
What is icu and ics in Acb and how many time icu or ics passes from breaker?
what size steel armoured cable is required to support 1500kva capacity. would 70mm squared be enough or would I need 90 or 120mm squared 3c plus earth
advantage of motor design on higher power factor . normally motors are designed for .8 power factor. what is advantage of designing at .88 power factor
Where I can get the sample question for post of Junior engineer electrical-II For RRB Bhubaneswar.
How much no load current of synchronous motor
What are the applications of autotransformers?