pressure switch range 0 to 2bar.i have to install from
ground level to 5 meters height.what is the formula the to
increse the range ? and every 1 meter how much pressure
should be add ?
Answer Posted / rajkumar.diice
At first you
should know
clearly the
correct fluid
density. If you
are working with
water; the water
density is
1000kg/m3.
Multiply this
with the tank
height 5 meters
then the
pressure acting
on switch at
liquid level 5
mts will be
5000mmWC, set
switch setting
at .5 bars. If
you are looking
to switch a
motor off
automatically
means use NC
contact.
| Is This Answer Correct ? | 11 Yes | 1 No |
Post New Answer View All Answers
What is difference between “Fault Tolerant” & “Fault avoidance” PLC? Application where these system s are used?
What do you know about gail?
Dear Friends, we are planning to design Power distribution and Fiber optic in the same cabinet.Like Front side Fiber optic and Rear side Power distribution.Is it any possibility of problem occurs like interference etc? Your answer is highly appreciate.
What is solenoid valve? Where it is used?
How does temperature bath work? How does coil gets heated only by applying some current?
where proximity sensor installed on tank in loading arm application
Q- What are the application in which PNP transistor is preferred over NPN ?
what is IEC code in cables & how to selecting cables?
principle of dead weight tester ?
1.what is controller proportional gain 2.what is the controller intergral action time. 3.A proportional plus derivative controller that has a proportional band of 20% and a derivative action time of 0.1 minutes. Construct the shape of the output waveform for the triangular input if the input rises and falls at the rate of 4 units per minute.
what is RTV function in in process control?
How do bending tubing provide better measurement than using tubing fittings such as elbows?
How can a d.p. Transmitter be calibrated?
key exchanges in wpa,wpa2,tls
what is sliding spool valves?