Answer Posted / k.prakashchandra
Stored energy = V x AH watt.hours Back up time in
hours=stored energy/load in watts.If the batteries are in
series total voltage is to be considered and if in parallel
total AH is to be considered
| Is This Answer Correct ? | 3 Yes | 2 No |
Post New Answer View All Answers
why we can stote dc? why we cant store ac?
why i can not use thimble on capacitor duty contactor
what is the purpose that we use PLC system in power system
What is the disadventage of gland earthing(power cable) if any. ?
is the value of inductance depends upon the evalue of thitha in doubly excited machine?
what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks
What are the Return ( Monthly / quarterly/ Annual submitted to Electical Inspector for an establishment (Factory in Maharashtra-- Small scale category having seperate HT line of 22KV ) as per Maharashtra Electricity Act
A logic circuit that provides a HIGH output if one input or the other input, but not both, is HIGH, is a(n)?
Could you measure voltage in series?
In EHV transmission line a neutral grounding reactor is often placed at neutral point of shunt reactors. What is the recommended protection for this neutral grounding reactor? Should I use a fast closing switch to bypass neutral grounding reactor when this protection operates?
can we start slipring motor on star delta like we start induction motor ? if yes where will we connect ?
How to calculate per unit impedance of transformer?
what is a pulse transformer? how rise time of pulse changes when ever the voltage changes?
Write a note on Treatment for electric shock.
what is meant by neutral compensation factor and where it is used