Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

What do you mean by class of CTs and what is the meaning of
cl 1.0, cl5P10, cl 10P10 CTs?

Answer Posted / k.prakashchandra

1.0 class is for measurement 1%- error at full load.Other
two are for protection. 5% error at 10 times the rated load
and 10% ---

Is This Answer Correct ?    4 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

which type of effect of turbine and generator reverse power protection ?

4197


How is operate breaker failure scheme in substation

2128


CAN U PLEASE TELL ME SOME G.D TOPICS FOR APGENCO INTERVIEW&G.D

2415


Pls mail me utility & Dg related question with answer

1795


what is the responsibility of C license holder in industry?

9170


What are stable systems?

1104


what is doubling factor in making current of a breaker?

2074


My question is whether bellow formula is correct to find bus size for 46kA for 0.5 second & what is RT in bellow formula. formula to calculate the size of busbar to withstand the thermal stresses due to currents with duration of 0.2 sec to 5 sec. Sp = RT( I x I x t) / K Where Sp – is the cross sectional area of bus bar in millimeters. I -    is the value of AC fault current. t -    is the operating time of disconnecting device in seconds. K –  is the factor depending on the material of the conductor, insulation and initial and final temperature. Value of ‘k’ for copper is 143.

1889


DEFINE BREAKING CAPACITY OF BUSBAR & HOW IT IS CALCULATED?

5230


Is it possible to download the Siemens Selection Chart(TYPE 2 coordination) for 1) fuseless selection 2)Fuse selection

8242


What is the diffrence (Technical & Construction ) between CBCT & Normal CT?

2043


If the earth is a good conductor of electricity, why don't people get shocked every time they walking on earth?

1818


What are dcs and plc?

1112


What should be the protection scheme for a 15kw, 3-phase motor working in a lathe machine.

2075


On what cycle does thermal power plant operate?

1173