How the earth fault relay works please explain?????????
Answer Posted / avd
In continuation to above answer, there are different
schemes to detect earth fault in the system
1. By using residual connections of three phases CTs
2. By using CBCT
3. By using a neutral CT at transformer neutral point.
| Is This Answer Correct ? | 4 Yes | 2 No |
Post New Answer View All Answers
Dear Respected sir how to test ABB REX521 protection relay by relay tester.
my question is how to answer the question "you are from b.tech eee background and why do you want to go for banking
What are root loci?
What is difference between Sample test and Routine test in safety standard?
What is transmittance?
What will be the effect of circulating current in HT xlpe cable when both the armour ends are grounded. Will the termination fils after some time in case of 33 kv supply.
what are the pecularity of shaver sockets ?
what is the effect of vector group while phase sequence of a generator changes,whether the vector group changes or not
HOW TO SET THE EARTH FAULT SETTINGS IN ACB????????????
what kelvin's law ?
What is the effect on power factor, shown by a trivector meter; incase of reverse phase sequence. If the power factor of a system is lag what meter will show in case of reverse phase sequence connected to the meter. and What in case of lead.
How phase displacement change in the over current relay coils.
Damping resistor provided in open delta (tartiary) winding of a measuring PT at the incoming of a MV inverter drive panel is getting heated up. Can any body explain the reasons and suggest the remedy?
What are the ratings of VCB, MCB, MCCB, SF6, ACB, and OCB?
State The Difference Between Generator And Alternator?