what is meant by dielectric breakdown ? where we using HV
test kit & what purpose?
Answer Posted / sri
High-voltage transformers contain oil as their insulating
dielectric. When a critical electric field is exceeded,
conduction paths grow at microsecond speeds through the oil,
in the form of branched trees, called streamers. These can
lead to destructive breakdown.
Above a particular electric field, known as the dielectric
strength Eds, the dielectric in a capacitor becomes
conductive. The voltage at which this occurs is called the
breakdown voltage of the device, and is given by the product
of the dielectric strength and the separation between the
conductors
The high voltage test (also called dielectric strength test
or hipot test) can be made in AC or DC. If the high voltage
test is made in DC, it is then combined with insulation ;
if the high voltage test is made in AC, it is then, this is
then, more stressful for the sample and made according to
the sketch below.
Measurement of high voltage test under alternating current
is performed using an alternating voltage (50Hz) adjustable
to an effective 50V to 1,500V. As is the case with direct
current, the high voltage test detects any sudden rise of
current up to a programmed threshold.
http://www.sefelec.com/en/high-voltage-test.php
purpose
to test the insulators for their effectiveness. normally
used for transformer oil testing purpose.
| Is This Answer Correct ? | 3 Yes | 1 No |
Post New Answer View All Answers
What is state space method ? Why its used ? Can it applicable on linear, non-linear, 1st order, higher order, homogeneous, non-homogeneous, open-loop , closed loops , stable & unstable systems ?
What is the pro & con of having 11kv & 33kv incoming, and what is the adv & disadv. of converting from 11kv to 33kv.
Explain the working of variable frequency transformer?
Why is better to have a minimum ceiling voltage of 250% than 160%?
Why compensation is necessary in feedback control system?
What are the uses of lead compensator?
What is an ideal transformer?
What is the gross weight to copper ratio in slip ring induction motor of 4000 HP,6.6 kv, 372amp, 992 rpm GE motor.
Can 33kva/415v transformer be run underground? If the answer is yes why and if the answer is no why?
How can we findout the maximum efficiancy of Transformer? At which load?
What is the maximum and minimum rating of UPS?
In diesel generator how AVR get voltage to excitation. And basic diagram DG EXCITATION CIRCUIT.
How we can come to know the substation range,without go through any name plate ?
why do we measure VIBRATION in -24vdc and why we adjust gap voltage -9vdc to 10-vdc? i am trying to get this information since 5 years, yet i haven't get reliable answer, i hope i can get from you.
What is open loop and control loop systems?