1 Ton = ? amperes & power.
How much power 1.5 TON split AC consumes in an hour at 17
C , 26 C & 28 C (thermostat' temperature).
Answer Posted / randy
BASICALLY, 1 TON = 12,000 BTU
1 WATT = 3.412 BTU
THEREFORE: 1 TON = 3,516 WATTS = 4.713Hp
CURRENT (Amp) I = Power (Watts) P /Voltage
(volts) V
I = 3,516Watts/240Volts
I = 14.65Amperes
The ans: a)P=3,516Watts
b)I=14.65Amperes
| Is This Answer Correct ? | 77 Yes | 99 No |
Post New Answer View All Answers
We have 750KVA DG set, we want to introduce REF relay with 1250/1A,CL PS,Current transformers.The lead distance of 2.5mm copper flexible cable from CT to relay is around 5mtrs.We would like to know the knee point votage(VK) & IM calculion for CT's
What is voltage ratio of a transformer?
What is the difference between PLC and Embeded system
Please define ohm’s law for a.c (alternating current)?
what is the difference between c power and U power acb breaker
please give me solution to rectify the emi(electromagnetic interference)
why can we use cosine wave instead of sine in ac supply as both have same rms vale and ripple factor
what is meant by residual over voltage & residual earth fault ?
State the points to be considered for selecting a particular type wiring.
What will be the current if the resistance total in a series circuit doubles?
how does it help for selection of a transformer.
in battery charging room we find two fuses (one in positive other in negative cables ).why it is so?one fuse is ore than sufficient?
How to choose the vector group for the step up and step down transformers??? Tell me the which vector group is suitable for step up and step down transformers and whats the reason to choose and whats the benefits???
What are the difference between normal application Transformer and Solar application Transformer?
What Is HO factor in power selection