What is difference between earth leakage relay and
restricted earth fault relay ?
Answer Posted / ramesh baba
Both Earth Fault Relay & Restricted Earth Fault Relay works
on the same principle, i.e. when fault current flows faulty
section in to the protective relay they will sense the
fault and trips the circuit.
But the main difference between these two relays is,
*** The earth fault relay will protect the system against
any phase to earth fault. But it can't sense the leakage
currents flowing throgh the neutral.
*** For sensing of over currents or leakage currents
flowing throgh the neutral , the restricted earth fault
relay is used.
| Is This Answer Correct ? | 4 Yes | 2 No |
Post New Answer View All Answers
what is diff btw electric,magnetic & eletromagnetic field
in parallel operation of power transformer why the distance between power transformer and capacitor bank feeder is necessary to know
what is the role of transistor in Circuit?
draw vector diagram and +ve,zero sequence diagram of symmetrical three phase fault.
what is meant by CT`s saturation ? Can we use Metering CT`s with Protetection CT`s ?
what is ground fault in ACB?
can u give me a brief idea about power line carrier communication ??
1.ZEBRA conductor(large size) 2.KUNDHA conductor( small size ) 3.panther conductor(very small ) 4.lepard conductor (very very small)
i want bhel placement paper for electrical if anybody having pl send to my id kavitha867@myway.com immediately
1.why we are using blocks in withoutgaplightning arrester 2.why we ar using bushing in withoutgap lightning arrestor
why do you add the load short circuit impedance when considering short circuit amperage. It seems that you should only consider supply. If you need to consider loads and you don't know what loads are to be added , what would be a good sub-transient reactance rating for the loads?
What are the protection required for Transformer, motor, Line, Generator, capacitor, that all i have to refer which standard?(Like Transformer detail IS 2026)
what do you mean by type zero control sytem ?Give an practical example of type zero contol sytem?
what is the physical connection of a analog i/p to a analog i/p module (ab plc)and through a analog o/p module(ab plc) to a analog o/p . and how all the process control by scada
how we can set the IDMT relay.