what is the KVA formula of a three phase transformer
Answer Posted / tanmay chatterjee
output KVA=1.732*V(OUT)*I(LOAD)
INPUT KVA=3*(supply voltage)*(primary side line-current)
| Is This Answer Correct ? | 8 Yes | 3 No |
Post New Answer View All Answers
what is the formula for efficiency of francis turbine and generator for hydropower? what is best way to select francis turbine and generator?
is that a problem if i connect a single phase load to a secondry delta connected transformer but i get a neutral from other transformer i the system?
Is neutral transformer can be called as control transformer?
If any cable burnt how can we identify it burnt by high current of high voltage?
Is there any Electrical supervisor license which gives permit to work whole India rather than individual state??
Electronic circuit
If a transformer primary winding operates at 240v, the secondary at 120v and the load is 1500w & the transformer is rated at 92% efficient, what's the current flowing through the primary winding of the transformer? What is the formula for finding this?
what are the necessary basic electrical topics to learn for mechanical engineer to deal practical problems.
Diagram on interconnectivity of 11kv transformer with RMU (i.e, one incoming and two outgoing or two incoming and one outgoing)
RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV is ok ,but haw to calculate the KA rating?
(1)WHAT HAPPENS WHEN SUDDENLY LOAD GIVEN TO THE INDUCTION MOTOR ? (2)CAN WE MAKE WOOD AS MAGNET ? (3)WHAT IS THE VALUE OF MAGNETIC FLUX DENSITY IN TRANSFORMER ? (4)WHY WE ARE USING ELECTROMAGNETI NOT ELECTROSTATIC IN MACHINE ?
Explain Even and Odd signals?
What is acsr cable and where we use it?
which cable is used for 15 Hp monoblock pump 3phase and service wire Distance is 210 feet please tell me cable size Armaured
what is the basic need of domestic loads 1- voltage 2- current