Can earth resistance be measured without connecting the
earth electrode?
and should earthing connections be disconnected
What is the effect of connecting two cables of different
sizes in parallel with supply?
Thanks in Advance.
I am intrested to get in touch with some
tecnocrats/engineers,my mail i.d is :
hiremathvijay@rediffmail.com
Answer Posted / k.prakashchandra
Earth resistance of an electrode is measured without its
connections.When two cables are used in parallel,the cable
having lower resistance will share more current so that the
pd in both cables will be equal.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
What is stacking factor? What is its approximate value?
What do you understand by oldham's coupling ?
How to calculate cable size by using load.?? Any formula...
what is 30-phase of transformer
i will applied in 1U-1W on 440 volt primary delta side. what is the result of magtic balance test
what is buffer resistance starter.?.What is the working principle and where it is used..?
acb(AIR CIRCUIT BREAKER)NOT CHARGING AUTO
Comment on the working principle of operation of a single-phase transformer.
what is per unit calculation?looking for simple and strong explanation thk u
What is bode plot?
Is any generator is developed which is operated with out diesal or other expensive source?
In Dyn11 power transformer if any one of the 3 phases connected to earth in star connected side then please explain effect of the current flow in delta connected side of transformer.(In this case if one phase is shorted to ground in star connected side then we observe the current flow in two phases only not three phases in delta connected primary side. Please explain why it is so?)
difference between Ac and Dc mcb ????
Is it possible to measure the voltage of a battery from a single terminal?
Explain the advantages and disadvantages of thermal power plant?