What is the meaning of TRI Vector meter?
Answer Posted / ramesh.a.eee
Trivector meter is Electronic type Energy Meter which
measures energy parameters, like active energy, Reactive
energy,apparent energy, Power Factor, frequency etc.
Through which we can know how much enregy recieved or
sent.Trivector meter has 2 types, one is 3ph 3wire meter n
other is 3 ph 4wire meter.
It is conneceted in the substation to incoming or outgoing
feeders to know how energy is given out or recieved from
other end, or to Transformers on HV n LV side to know the
Transformer loss.
| Is This Answer Correct ? | 23 Yes | 1 No |
Post New Answer View All Answers
how withstand of hi-pot test outputs of transformer wire 2.5mm
What is the accepted limit to increase the choosen transformer capacity over the load and why ?
If the feeder rating is 7.5 kw or 10 HP star-delta feeder, MCCB is taken as 63 a, contactors-32 a, how much will be the OLR rating or which range OLR should be considered when we concern about type-2 coordination?
Safety of on line ups
Operation carried out in thermal power stations?
I need a formula to calculate the size of cable as per load but in the terms of length. Please Reply me as i search lot of sites but i did not get the answer.
Enlist four components of electrive drives.
When we use 3 terminal resistor?
what is stper motor
why we are not giving the zone 1 trip command to the master trip relay
What is a copper loss or i2r loss pc?
What are the relays in ACB and VCB
What are the advantages and disadvantages of open loop control system?
A well system is when , no. of bus bar is less or more. Tell me the concept of it.
What are the protections for safe running of electric generator?