An electric bulb giving light but at the time of lighting
which one it takes? voltage or current
Answer Posted / vijayakumar.k
We need both voltage and current acoording to the Ohms law
of V=IR,so the bulb glows only of the resistance of the
tungsten..so R=V/I
| Is This Answer Correct ? | 6 Yes | 0 No |
Post New Answer View All Answers
how to work droop ct in generating station
do we use links in a dc circuit?if so what s its use in it?
Define average demand?
why we use condenser in the thermal power plant, althrough the same vapour will be again heated
I have 2500KVA transformer delta/star,13.8KV/380V provided with LV 4000A breaker. Already I have 2300KW motor feeder with a full load 90%. Is it possible to connect another 1600A from that breaker? If so how the calculation is done?
why do we carry out winding resistance test?
Please, if 1kw is equal to 1.25kva; how then do I know how many kva in 7.5kw?
any body,pls tell me how to done relay coordination ? how to coordinate by TCC curve?how to read the tcc curve?
what is W.T?specify the acceptable range?
If SFU is Switch Fuse Unit, What is the expansion for FSHF in Electrical Engineering?
is there any chart showing the suitable cable size according to AMP and length ? for three phase motors
What happens if we give the supply to the rotor of induction motor and make its terminal shorted?
how to caculate cable size for diff types of loads? if anyone know the calculating procedure please tell me
What are the different types of hydro schemes?
In both 600/1000 V cable and 450/750 V cable, we can supply 415 V. However for distribution, all utilities are using only 600/100 V instead of 450/750 V. What is the reason?