Answer Posted / mohamed yousuf
i will give u an example how to calibrate the pressure
transmitter,if u calibrate the pressure transmitter in the
range of 4 to 50psi, by using the hart callibrator we can
clibrate it
step1:apply the preesure of 4psi and adjust the transmitter
to 4ma
step2:apply the pressur of 50psi and adjust the transmitter
exactly to 20ma this is called span setting
| Is This Answer Correct ? | 12 Yes | 3 No |
Post New Answer View All Answers
What is the differerence between hysterisis and linearity.
can anyone tell me about the basic concepts to consider before to start a PLC panel wiring
If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , so what to do for solve this problem. The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?
can anyone guide me how to get any of the previous year GAIL question papers? are they available? 0n 2nd august i have to take the written test.
what is a good line as ic engineer as maintenance ,oc, project, calibration ,validation engineer?
how to change measuring units from mmwc to cubm/h in rosemount air flow transmitter with hart communicator fluke 744
Explain PID controller tuning & any one method used for it.
In turbine what does term CDP, NI, NH, HSSOC means.
hi friends,im an instrumentation and contol engg student,can u hlp me of suggsting barc written question paper,my id is roysuvaranjan@gmail.com, cel no.9563591747
Definition of reverse and acting controllers:
What is the purpose of the analyzer in petrochemical plant?
There are two chlorination tonners both are connected to two pressure swithes and the pressure switch is connected to SOV which operates the valve to changeover the tonner selection i.e if pressure one tonner goes low the other tonner should come in line if it is inautomatic selection design a circuit using relays ?
What happen if I install my pressure transmitter below the elevation of pipe in natural gas service?
hello friends, can you please send me the model paper or question paper to be prepared for hpcl examinations????????? You can mail me at rahim_here@yahoo.com waiting for your reply........... help me .. plz.....
Draw a P& ID showing – orifice flange, plate, dp transmitter, isolation & bypass valves and tubing.