what is the working of loss of excitation relay (40G)? how it
is work?
Answer Posted / k.prakashchandra
LOE relay acts ,as its name indicates, when excitation fais
either due to field breaker(FB) opening or some other
cause.When there is no excitation the gen will run as synch-
motor or induction generator if the prime mover still
running. In both the cases current will be drawn from the
system ,hence power flow is reversed .Then the relay acts
to actuate the master trip.Earlier this relay acted only
when FB opened, closing a switch in the opened position .
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
compare between starting charactristics of synchronous motor with those of 3Q Squirrel cage induction motor
please explain how to do 'pole drop test' on generator?
Percentage losses in power generation?
we all know voltage is a force(emf), and the force always devides if 2 or more than2 loads are there but why does the voltage remains same is parallel, it must devide na ???
How to know about the rating(voltage and other) of induction motor if its name plate is missing at the manufacturing site.
how to calculate the loss tangent of electrical cables
Why single phase induction motors are not self starting ?
how we arrange the hv side with delta connection in case 33/11kv of transformer.
Can anybody tell abt concrete encased earthing or grounding?
he compression ratio for a petrol engine generally lies between
which protection used in power plant?
What is the actual calculation for transformer short circuit test?.
What is the difference between Encoder and Resolver?
Define demand factor?
who invented active elements? plz give me the complte details of active elements...