What is the advantage of Neutral graunding transformer
insted of Neutral graunding Resistance in generating
station explain briefly.
Answer Posted / amit khamesra
NGR and NGT serves the same purpose of limting the earth
fault current to the rated values which basically depends
upon the core damage curve of generator. Differece is NGT
gives earth fault protection of 100 % winding whereas NGR
protects only 95% of the generator winding. Potential
difference of the 5% winding (towards neutral) with respect
to neutral is very less so the earth fault in that region
of the winding is not sensed. This is avoided in NGT using
sensing of 3rd harmonic under voltage based principle in
secondary of the NGT.
| Is This Answer Correct ? | 3 Yes | 2 No |
Post New Answer View All Answers
A double circuit with dog conductor 66KV Transmission line from wind farm evacuation to feeding substation having capacity of 25MW for transmission. Can same transmission network be considered for further expansion of Power & how much in MW. If we need to expand next 10-15 MW more will there any augmentation is required in transmission network? Kindly reply asap.
what is the requirement regarding earthing of Single conductor with AWA
why current flow to the opposite direction of flow of electrons???????????
What is the cut-off rate?
What is the settings of distance protection relay in 400 kv line
whate is the meaning of balance/unbalance,in stabilizers type
WHERE CAN I GET THE PREVIOUS QUESTION PAPERS OF Govt Polytechnic in deee 2nd year papers
What is the permissable nutral current of three phase system as per IS standards?
What happens if the series current double?
In our plant we have installed new MCC with ELR and CBCT which is detecting some leakage current in the system but it leading to some confusion when to check that in which feeder which is drawing current we put off the whole panel itself but still CBCT detecting some leakage current so can anybody ans me , where i am going wrong or how to detect whether its actual leakage or CBCT malfunctioning.
What is the type of earth fault protection used in battery? explain.
Good morning: I'm looking for some informations about the OLTC or the LTC: I wont to know what the function of the tie-resistor in during the operation of reversing/coarse operation Cordially
Define settling time.
Write the programming software name for LG, SIEMENS,Messung,AB
what is apparent poewr, reactive power, & active power?