How can you justify a fully carged battery by physical
checkup ?
Answer Posted / bhavani prakash
1) By Measuring its VOLTAGE by Multimeter, in case of 12V
battery, it should be between 12V to 14V.
2)By Measuring with HYDROMETER, the SPECIFIC GRAVITY value
should be between 1.19 to 1.4
3) By Measuring the TEMPERATURE that should not exceed
above 41 degree C
In case of VOLTAGE is lower it should be charged with a
CONSTANT CURRENT or CONSTANT VOLTAGE CHARGER to reach the
specific voltage of battery.
In case of SPECIFIC GRAVITY IS LOW, the distilled water
should be added to all the cap holes to certain distances in
the battery and then charged.
If the water and sulphuric acid in the battery turns black
then the battery is dead.
A proper Ventilation should be arranged to limit exceeding
the TEMPERATURE of the battery in charging condition.
The Terminals of the battery should properly cleaned with
PETROLEUM JELLY.
The battery should not be placed under sun light.
It should be cleaned with wet cloth.
For any purpose the battery should not be SHORT CIRCUITED.
Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
we have a lot of model of rectifier but thyristor rectifier is the most rectifier that use in power system. Do you know why this rectifier is used?
if there is nutral in phase why we use earthing wire and grounding? even at fault condition the fault current flows to neutral (it is a lower path)
how to compute kAIC? with formulas...
How to measure size of cable on a given load
How REF protects transformer alone? explain with diagram.
Why is tan-delta test and capacitor measurement done on alternator?
how does directional relay work incase of ac ?
In motors how many types of cooling systems were used?
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
what is doid
What is the one main difference between ups & inverter ? And electrical engineering & electronics engineering ?
defination of lines
Can anyone explain me about the RLC based Impulse high voltage generator and how to and operation of Series resonant High voltage reactor...?
How to calculate multiplication factor in kva example 500kva ans pls ?
How to calculate the no of Ceiling fan (1200mm sweep) per unit area?