What is Procedure the procedure to select CT's & PT's in
66kV and above substation?
Answer Posted / prakash
You need to required following data
Voltage Level, Current, Protection Class, SC Current
Etc while selecting CT's & PT's
| Is This Answer Correct ? | 10 Yes | 1 No |
Post New Answer View All Answers
What is the difference between a Root Locus plot and a Bode plot?
how to compare with Relay settings for HT< panels, RMU panel, and PSS CSS transformer?? 1) Load amps, 2)Tripping time, 3) CT ratio, 4)Cable size 5) Transformer KVA rating 6) transformer full load amps
kindly send me 11KV MV motor differential protection procedure by primary injection method.
Is it possible to use a S1 duty class motor for crane application (S4)? If not, why?
Why it is possible to use PWM with a STATCOM and not with a conventional TCR based SVC
can anyone please help me to find the rupturing or breaking capacity in KA of circuit breaker (MCCB,VCB,ACB etc) of HT and LT side of a distribution transformer...please help with detailed step by step answer...thank you
how to calculate single phase motor efficiency ?
how oil in the MOCB was reduced compared with OCB? what are the features of the MOCB?
How to calculate wire length,size & current? ( related to control panel)
What are protections for dty type transformers
What is the maximum percentage voltage drop (vd%)for a motor control center
How a band pass filter is constructed?
How halogen & merquery lamp works.
What is the different between digital phase converter and ordinary phase converter?
how to CHECK CT AND PT AT THE FAULT OCCUR IN GENERATOR RELAY PANEL .