THERE ARE TWO TYPE OF CT USED
1) METERING
2) PROTECTION

IN THE PROTECTION CTS
THERE SUB CT/S BASED ON THERE FUNTIONING

5P10, 5P20 & PS

FOR 5P10 CT : 5 % error in the ct for protection current
sensing/measurement
p: is used for Protection purpose
10 0r 20 : The ct will withstand 10 or 20 time current of
the rated primary current of the ct e.g
300/1 it mean the ct will with stand 3000A, for 1 minute
during the fault sensing current

Is This Answer Correct ?    57 Yes 24 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is an ac motor?

690


When MICC cables used ?

1614


state the working of discharge lamp?

1576


at work i have a genertor/alternater what is the easyest way to work out if it is dc or ac?

1389


How To increase Knowledge Of boliler regarding To Only Electrical Field..

1153






what is thermal resistance of PVC Cable.

1362


Can Anyone suggest the Standards (IEC or IS) for selecting copper current density?

924


Define peak overshoot.

799


I have a drawing of a wound rotor induction motor for a crane. This crane motor has 5 forward speeds & 5 reverse speed implemented of course with different amount of resistance for each speed setting selected. What has got me scratching around is the fact that 8 of the 10 speed selections switch in uneven (unbalanced) amounts of resistances on each of the 3 connections to the motor's rotor.Can this be possible? I would have assumed this would produce unbalanced rotor currents and therefore vibration in the motor. I would greatly appreciate anyone's comments on this. Many thanks, Confused.

1412


WHY TERTIARY OF POWER TRANSFORMERS IS LOADED WITH EQUIPMENTS LIKE CT,PT,ISOLATOR AND CB

1469


What do you mean by phasors?

638


Would you recommend to replace all oil filled cables with xlpe cable for hv transmission with the current technolgy for xlpe cable?

1066


how ups works ? various parts of ups and working principle

1473


What is the dependency of stiffness on load angle??

836


A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is observed the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?

1743