WHAT IS RMU & HOW IT WORK,IT USEFUL FOR HT OT LT POWER
DISTRIBUTION MAUFACTUERE IN INDIA.
Answer Posted / ankur
RMU-Ring Main Unit
It consists of Isolator-Breaker-Isolator configuration.
The RMU is used in the 11 kV HT Power network.
The RMU is using SF6 gas for the arc quenching medium. All
the two isolator and one breaker are in the one chamber
having SF6 gas.
The breaker is having O/C and E/F protection using relays.
The isolator is being used for the operation on ON LOAD due
to the SF6 gas medium.
| Is This Answer Correct ? | 8 Yes | 1 No |
Post New Answer View All Answers
which type of motor is used in automatic swing gate
what is meant by directional earth fault and non directional earth fault? describe both.
hi everybody how to design string combiner box (scb) internal parameters like bus bar and spd (surge protection device and fuse which place to set that,and also bus bar one particular cross sectional how much heat generated and how much power loss tell me Clearly and briefly
we have require a Motor (1500kW, 6.6kV, 50Hz) which shall operate at 1500rpm during 30min and after it shall run on 500rpm during 15min. The same cycle shall be repetitive during the whole working days. Which method is best and economic to achieve such type of task. VFD, VVFD, Pole changing motor etc.
Dear sir, iam completed iti ncvt electrician 2000-2002 & diploma electrical eng completed 2008-2010 distance education in rvd university, still i got B licences only but my working company want C licences, how to i get c licencese pls reply me iam in critical situation thank you karthick 9841637803
Factory acceptance test. FAT. For 132 kv transmisstion towers what is that meaning and what are the tests commonly companies perform now days.
why we cannot protect 100% winding of an alternator by using differential protection?
Does the direction of rotation of d.c. Shunt motor would get reversed if the armature current and field current both are reversed?
What are the types of class b amplifier?
how does grading rings & spacers in transmission line works? Working Principle?
WILL SCHNEIDER MAKE ACB(MASTERPACT)TRIP ON REVERSE POWER?
I want to merge a cable..in between two metering Cubicals which contains CT's and PT's and Energy meter..before taking merger..what are the common things required?
What is the meaning of dedicated earthing?
what is meant by vector group of a transformer? How can it be derived?
How many sprinklers should be in one pipe line?