what is the formula to find battery back up of ups?
Answer Posted / mahesh
LOADED UPS KAV/BATTERY LOW VOLTAGE=I(DC)
THEN SEE THE BATT. CAPACITY
FOR EXAMPLE 100AH BATT. AND DC CURRENT 100AMP
SO BACK UP IS 1HOUR
| Is This Answer Correct ? | 3 Yes | 1 No |
Post New Answer View All Answers
What is force on a conductor in a magnetic field ?
Rules and standards of electrical control wiring ?
why we use Test Terminal Block in 11 KV and 33 KV electrical panels.
what is a vector protection in transformer
if we have a industrial load of 400 kilowatts with 415 volt AC then how much total harmonic distortion (thd%) should be acceptable for steady power system.
What is the lifetime of a Thyristor? Is there a recommended lifetime for thyristors after which they should be replaced?
which pump used in WTP explain the function of VFD how to dtermine capacitorbank of capacity one plant
how test transfomer(3 phase75kva) by megger
What is the difference between cylindrical-type and sandwich-type winding?
tell me about eletrical contractor
which cable is used for 15 Hp monoblock pump 3phase and service wire Distance is 210 feet please tell me cable size Armaured
Block diagram of Power line communication?
How maesure earth neutral value & how much maximum value value required in between earth & neutral.
Why it need to form a capcitor when it not been in use from three or two year. Plz describe it technically.
What is the basic rule for block diagram reduction technique?