what is the difference between delta-delta, delta-star
transformer???
Answer Posted / virendra
Delta - de;ta transfomer is used at Gnerating station or a
receiving station for Change of Voltage , generally it is
used where the Voltage is high & Current is low.
where Delta star is a distribution kind of transfoemr where
from secondary star neutral is taken as a return path .
this configuration is used for Step down voltage phenomina
| Is This Answer Correct ? | 26 Yes | 0 No |
Post New Answer View All Answers
What is excitation in case of dc motor?
what is submersible pump?what is different between motor and sub motor?
If a 3 phase induction motor is in off condition in the conveyor and rotor of the motor keeps moving with the conveyor than the resistance of windings of motor varies. why is it so ??
What is milivolt dop test in Busducts? What is its significance & procedure to do the test?
How a capacitor discharge weld power supply works? what is the use of a pulse transformer?
The 3 phase 400 hp 440 volt slip ring induction motor do not take one phase amps why ? The motor is running good condition
if flux and load static in dc motor and supply voltage increases 20% then what happened in speed
what is the difference between 4pole & 6pole DC Motors & give advantage ?
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
How line capacitance & line inductance varies with increase in height tower.
full form of flry b
what is the range of maximum DOL and SDS can be use for pump and fan application
tell me about roaster switch .& what is the function in transmission & distribution?
WHY IN AC DRIVES,INPUT PHASE CURRENT SHOW UNBALANCE?
what about SAP/MRP regarding manufacturing of electric motors and all drives?