can three phase induction motor rotate with only 2 phases
connected
Answer Posted / ashok kumar
with 2 phase motor does take place of rotation but motor
should not be loaded .it will start or rotate with humming
sound.after get start the motor, we can load it, but only
with in a limit(which is much smaller then that is in normal
condition) if we loaded the motor with in limit (with in the
range of full load current)it will be continuous in rotation
but its torque will be reduced as well as speed and also
effected its efficiency.
| Is This Answer Correct ? | 0 Yes | 1 No |
Post New Answer View All Answers
What is K-rated transformer? What is the use of it? What can be the size(pls provide calculation if possible) of K- factor transformer for 550kW,690V motor operating with drive (VFD)?
Why insulation level follows this order? transformer < bus bar < circuit breaker & Isolator < transmission line.
What types of high speed CMOS circuits have you designed?
How can two 3 phase transformers of same KVA and Voltage be connected in parallel?
how to select electrical equipment such as fuse,dg,transformer,motor,msb,wire,cable as per the connecting load..please mention any books to design,take licence
how to extend relay operating timing in 24V dc relay card (without using Timer )
how to calculate the tarriff for an industry whose kva demand is 10 mva
how to calculate energy of 3-phase motor?
why burdens of VTs is more than CTs?
what is meant by moulded case circuit breaker ?
What is lc oscillator?
What is the difference between Delta & Wye windings?
Why derating factor os applied on Cables?
How to design pavement quality concrete by using C.R.C.P Method
in 132kv substation CRT means