what type of relays used in transformers?
Answer Posted / sethu siva & mainkandarama
1)Differential protection (If transformer is more than 5
MVA :As per IS 2026)
2)Restricted earth fault protection
3)Stand by earth fault protection
4)O/C & E /F protection (if required)
5)Over flux (V/F)
Auxiliary protections
1)B' relay protection
2)PRV
3)Oil temp. high trip
4)Winding temperature high trip
5)OSR
Alarms:
1)Winding temp. high alarm
2)Oil temp. high alarm
3)MOG alarm
Is This Answer Correct ? | 15 Yes | 1 No |
Post New Answer View All Answers
how to avoid Saturation in C.T?
What is the use of Surge Capacitor in LAVT?
300m long and 30kw inductive loade 3phase supply how many size cable required
Operation carried out in thermal power stations?
What is the Good Earth resistance value of G.I & Cu. Chemical Earthing & Normal Pipe Earthing?
33kv Rated output avilable in market (any where in india)
What are the three constants associated with a steady state error?
If we have to find the inductance of a dc shunt motor then by giving dc supply or ac supply and what is the reason for it. (this example is from "to determine the transfer function of a dc shunt motor ")
working principle of AC Servo Motor with its construction
How the over load setting for HT Motors calculated-provided in Numerical Relay
What is resistance of 50meters, 16sq.mm, single core copper cable?
How many points does a Circuit can have?
Difference between field rheostat and armature rheostat.
What is the formula to calculate the rating of a three phase miniature circuit breaker
what is the clear formula to calculate cable size for a load