how to find the 2500 KVA transformer rated primary and
secondary volt and current?
Answer Posted / teja
It is not possible unless u provide the input voltage u r going to give for the transformer and how much voltage u want as out put
however if u know input & output voltages primary and secondary current values can be calculated as fallows
2500 KVA 33KV/433V
Then primary current=2500/sqrt3*33=43.745A
And Secondary current=2500/sqrt3*0.433=3333.34A
| Is This Answer Correct ? | 10 Yes | 1 No |
Post New Answer View All Answers
we have 2.2kw,Y,3000rpm motor but 6leads found in TB what happen if we connect in delta?
How to calculate flow of water delivered by pump when pressure & size of pipe line is given
what is a vector protection in transformer
what is v/f control in VFD?
what are the available sizes of pin type terminal lugs in the market today?
Why Transformer Neutral having one earth pit ( more earth electrode resistance) whereas body have many earth pit ( less earth electrode resistance)?
Explain the operation of variable frequency transformer?
i karmveer bharti persuing b.tech . plz send me syllabus and name of reference books. for preparation of section eng.
Meaning of ingrace protection for motor.for ex IPXY
Why transformer used in UPS??
how the aircraft outer body and inner body is separated ?
How to calibrate or test an LT Air Circuit breaker 440 volts, 35 KA, 800 Amps ?
What should be the voltage between Neutral and Ground in secondary side of the step down transformer (230 V to 110 V) with no load condition?
Write the force balance equation of ideal spring element.
What happens if we run alternator on under frequency?