how to calculate knee point voltage of current transformer?
Answer Posted / sunny
Is the answer given below is correct?
For calculating knee point voltage there are two methods,
they are
1.Low method
2.High method
1.low impedance method
Vk=24In(Rct+2Rl)
2.High impedance method
Vk=4IsRs
Then, Rs=If/Is(Rct+Rl)
where
Is,In-Rated Sec. Current of CT
Rct-CT resistance
Rl-Max. one way lead reistance from CT to Relay
| Is This Answer Correct ? | 8 Yes | 6 No |
Post New Answer View All Answers
as a electrical student why should i hire you?
What is mathematical model of a control system?
WHAT IS DOL STARTER? HOW IT WORK? GIVE ITS CONTROL AND POWER DIAGRAM .
what is Anti-pumping?
why we use sinosidal voltage / current instead of others in system?
I NEED RRB APTITUDE QUESTIONS AND MODEL PAPER,PLEASE SEND MY E-MAIL joo28_eee@yahoo.co.in
I have a situation to design sub-Distribution board/Panel meant for feeding power sockets. In the incomer CAN i Take TP MCCB with Neutral Link and All the outgoing feeders with to sockets with TP MCCB and Neutral Link? P.S : My System is IT Earthing
How seriving & testing of the HT & LT breakers are done. What are the standard Ir values on which we can come to know the test is passed or failed?
How to select the gauge of wire for winding of motors? How to select number of turns for winding of three phase induction motor?
how freewheeling diode improves the powerfactor
Why is the frequency not changed during transformation of electrical energy in a transformer?
Why do power lines not short out when they fall into water?
what is the effect of connecting three phase supply lines to three phase auto transformer output terminals through a fuse of 10Amp and a circuit breaker (MCB). Is this connection permanently destroy the transformer?
can we use CBCT in neutral of solidly grounded transformer? in place of three phases we can pass only one phase which decreases the size of CBCT?
control & auxilary circuits used for circuir breakers