Answer Posted / bhuwnesh namdev
The Ferranti Effect is a rise in voltage occurring at the
receiving end of a long transmission line, relative to the
voltage at the sending end, which occurs when the line is
charged but there is a very light load or the load is
disconnected.
This effect is due to the voltage drop across the line
inductance (due to charging current) being in phase with
the sending end voltages. Therefore both capacitance and
inductance are responsible for producing this phenomenon.[1]
The Ferranti Effect will be more pronounced the longer the
line and the higher the voltage applied.[2] The relative
voltage rise is proportional to the square of the line
length.[3]
Due to high capacitance, the Ferranti Effect is much more
pronounced in underground cables, even in short lengths.[4]
| Is This Answer Correct ? | 9 Yes | 11 No |
Post New Answer View All Answers
What is the difference between single core 2 wire and single core 3 wire system? Which application we are using this? and for What purpose we are using this?
hi I have done 3 yrs diploma in electrical engg after 10+2. I have 16 years of work experience into design proposals sales and engg application development in LV/MV swithcgear and sub station automation field. I want to apply for immigration to new zealand but I am not sure whether I qualify or not since I dont have a degree. Can anyone advice? Thanks Riz
When calculating the speed of a rotor required for a particular frequency of synchronous generator we use the equation 60f/p Is this p is the number of pole pairs of rotor & do we consider the number of pole pairs in the stator is 1?
Either It Possible a dc Motor to Run On Ac Drive [ Ex : ACS 800 , Yaskawa F7 ] If it is Possible How Pls Inform Me dinesh_elect_eng@yahoo.com
I am having a 42KW 3 phase electrical heating furnace, heating element is 80/20 nichrome material, my connections is made in such a way that 2 star connection compromising 2 coils per phase so totally 12 coils, shall if i use it unbalanced star condition (instead of 2 group of 3 phase or 1 group of 3 phase, connecting 4 phases of 5 phases) what will be the consequences and is it acceptable?
how to copy from plc ge fanuc versamax series,all input and output, adress, and printout.
CAN U PLEASE TELL ME SOME G.D TOPICS FOR APGENCO INTERVIEW&G.D
how to setting Load amps tripping time and extra settings for load Transformer protection relay with RMU panel using C&S model relay..?
whats the existence of reactive power and when it arises?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
How to do stting of vl250 siemens MCCB
How much ph is maintained of water electrolyte which is used in LRS for 1200 kw slipring induction motor ?
describe the fully control circuit diagram of ac drives
What is the direction of current flow in ct secondary...means if the current is flowing from P1 to P2 then what will be the direction of current flow in ct secondaryw
In synchronization circuit what is the function of Interposing voltage transformer(IVT)and Reverse voltage transformer(RVT)