how to calculate knee point voltage of current transformer?

Answer Posted / pankaj joshi

I am not familiar with the term saturation test but it seems
from the above posts like an exciting current test to
obtain the knee-point of the CT. With this test you can also
obtain the exciting curve (mag-curve) of the CT.

You'll need a variable voltage, (easiest obtain from a
variac - must be able to obtain the suitable voltage) a
voltmeter, an ammeter, a pencil and paper.You'll have to
measure the voltage and the current while you do the test.
Apply the voltage to the secondary winding with the primary
and other windings being open-circuited. Increase the
voltage until you reach a point where a small increase in
voltage results in a big increase in current.
Now slowly decrease the voltage to a few measuring points,
while you measure the current. (write it down) Something like:

205V - 1.1A
200V - 0.6A
190V - 0.238A
180V - 0.149A
170V - 0.114A
150V - 0.08A
125V - 0.061A
100V - 0.049A
50V - 0.028V
25V - 0.017A
0V - 0A

You have to decrease your voltage slowly to zero volt to
demagnetize the CT-core.

BEWARE The knee-point voltage will depend on the size and
class of the CT, and it can be very high on some CTs
(several hundreds of volts) Be very cautious, you will be
working on live equipment during the test.

Now you can just plot the current and voltage values on a
graph. This is the mag-curve of the CT. IEC classify the
knee point voltage as the point where a 10% increase in
voltage results in a 50% increase in current.

Is This Answer Correct ?    50 Yes 10 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

which pump used in STP

1658


What is the physical significant of power factor?

1482


As we use capacitior bank in 3ph ckt for improvement of PF, why not we use capacitor in single phase domestric use, at our house their are many inductive equipments,like fan,mixer,tube choke,air conditioner they also draw PF... by using capacitor can they improve PF. if yes--what are advantage and how to connect a capactor in single ph,and which type of capacitor if no- what are disadvantages.

1385


how calculate gd2 of ht motors

1822


Why the magneti fields are not passes from southpole to north pole

1643






what is the criteria for selection of conductor used for ehv ac electrical dischrge

1603


in general it is observed in power stations, the tertiary winding is used in higher rating Y-Y auto transformer but not in Y-Y power transformer. is the tertiary winding is compulsory then why it is not using in power transformer 

1287


how many parameters can integrate with fire alarm basically ?

1490


how do i work out the Amps of a incommer if i am running 1 37 KW motor and a 0,75 KW motor and some solinoids

1415


What is the angle of inclination for the oil connection from transformer conservator to Bucholz relay and why?

1693


what will be the effect if you were using different brands of outlets?

1466


We need to current density & short circuit calculation at 65kA for aluminium & copper busbar.

1238


What do you mean by power transformer?

639


how to get electrical supervisour certificate in gujarat

1521


explain the Trip supervision circuit

1654