how to calculate knee point voltage of current transformer?
Answer Posted / pankaj
The knee-point voltage will depend on the size and class of
the CT, and it can be very high on some CTs (several
hundreds of volts) Be very cautious, you will be working on
live equipment during the test.
Now you can just plot the current and voltage values on a
graph. This is the mag-curve of the CT. IEC classify the
knee point voltage as the point where a 10% increase in
voltage results in a 50% increase in current.
| Is This Answer Correct ? | 13 Yes | 3 No |
Post New Answer View All Answers
explain different types of d.c motors?
How we can come to know the substation range,without go through any name plate ?
what is the ground fault relay,which purpose it will be use,clearly tell me plz
How to calculate cable size in HT AND LT
11 kg trivevter meter has rating of -/5amps. And pt ratio11000/110v and is connected with 11kv ct/pt unit of cr ratio 75/5amps. And pt ratio of 11000/110v while checking accuracy of meter with HT Accuchek meter what value of PT ratio and CT ratio to be filled in Accuchek meter
if there is nutral in phase why we use earthing wire and grounding? even at fault condition the fault current flows to neutral (it is a lower path)
how the characterstics of control valve being done
How to calculate the current of Highpressure Mercury Vapour Lamp?what is the basis?whether we have to consider power factor or not?
What is signal flow graph?
what is p.s impedance measurement test in earthing transformer?
I have 1500/1A CT If i connect this CT in 6.6KV bus bar means what will be the voltage present in CT?
can i use the six sigma method which is used in management area, in state estimation of power systems?
Where burned of electricity,when,who, & why.
Why neutral point is consider as zero potential?
What is different bewteen low or high impedance busbar protection scheme