how to reduce power loss when the tranmission under long
distance?
Answer Posted / ch.phani
to reduce power loss in transmission lines
1)the voltage will have to be increased .but there will be
limitaions for this also
2) the distace between conductors should be as long as
possible to reduce inductance in case of ac transmission
3) highly conducting meterials based on the economy have to
be taken such as aluminium
4)power factor should be more .the more the power factor is
the less the current is .so losses are reduced
5)hvdc transmission is also another option
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
which phase is preferred for connecting 1 phase vt used for synchronizing OHL? WHY?
What is the Surge suppresor? Why using in a UDB's and How it works?
Is it possible to connect a safety device in to parallel?
What is evaporator & condencer & compressor
why the field winding in dc motor is not short circuited eventhough dc supply is applied across the winding
What is meant by rotor?
What are the commonly used schemes for the bus zone protection?
wat is meant by PX class in ct?
what is conductor copnstant of ab cable
what is active power & reactive power?
Shall I use 40A semiconductor Fuses in 32 A SFU ? Frame size is same. What Happen if Fuses burn on SFU?
Why we do 2 types of earthing on transformer (ie:)body earthing & neutral earthing , what is function. I am going to install a oo kva transformer & 380 kva dg set what should the earthing value?
what is the terminal voltage of dc series generator running at rated speed at no load?
How to set a Zone 1 distance relay for distribution feeder?
what is the use of the puls transformer in UPS & how it works???????????