what will happen if one of the phases from a 3-phase motor
is disconnected?? stop/run at 2/3rd speed or run at same
speed????
Answer Posted / niranjan
The motor will keep on running for a while but the current will rise on the other two phases and the overload relay will fall out, if its properly set and the motor will stop if the overload relay is set to high the motor will burn out
in the start Motor will start to shake the if there is no protection devices for over-load on the motor it will simple explode:)
Three-phase motors also vibrate less and hence last longer than single-phase motors of the same power used under the same conditions.
| Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
by using pump duty, how we will can calculate the motor duty(KW)? is there any standard or formula.
difference between Ac and Dc mcb ????
Either the Armoured Earthing strip of HT 3 core cable have to pass through CB CT or not , why ???
circuit diagram of trip circuit supervision relay
What is meant by stator? What is meant by rotor?
State the formula for overall efficiency of thermal power station
In how we connect watt meter for open & short circuit test of a single phase transformer.
WHAT IS counter flux IN CT?
How to calculate wire length,size & current? ( related to control panel)
what is the difference between linear choke and suction choke?
what is die electric strnth of transformer ?
. What is Electrical Life & Mechanical Life of Circuit Breaker? 2. What is Electrial Life & Mechanical Life of Magnetic Contactor? 3. What is RCD, RCCB & RCBO? 4. What is the Between defferance of RCD, RCCB & RCBO?
What is different type of Electrical curve and how it protects the equipment's while up-normal situation?
What happens to voltage when current is zero?
What will happend if given Vfd out put to step up transformer