Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

what is MC 61 relay

Answer Posted / praveen

3 Phase O/C + E/F + Highset
0C 0
50/51 RYBN
Numerical Relay
Lowset O/C -Is
Highset O/C -Ihs
Lowset E/F -Os
Highset E/F -Ohs
O/C Is = 20-200% Step 5%
E/F Os = 5-80% Step 5%
HS O/C = (0.2 to 40) x In step of -
0.2 In or disable
HS E/F = (0.1 to 20) x On step of -
0.1 On or disable
Time Characteristics available -
NI, VI, EI, or Definite Time
TMS : 0.1 - 1.6 Step 0.05
Site selectable Trip time Char.
Highset can be disabled
Display of Currents, Trip count
Self supervision feature
£ 0.25 VA on CT/Phase
Not applicable
0 to 60 C
< 2kg £ 10 VA
1 N/O Contact for self suprvn
Draw out
121 x 158 x 224
113 x 142
20-110V AC / DC or
88-264V AC / DC
1 AMP or 5 AMP
(site selectable)
4NO or 2NO + 2NC

Is This Answer Correct ?    15 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what are the advantages disadvantages of connecting high voltage block( 1:1 transformers) transformers between the turbo generators and busbars.

2071


what type of earthing do for dry fissure rock?

2418


Is it true online ups having bypass mode if it is true then why we called ups because it is interrupting power when goes in bypass mode

1979


by what factor the starting current is used when comparing star and delta connection for motor starting?

2038


impliment (AB)`+C to transistor representation

1805


When steam condenses and becomes water at the same temperature, the specific heat for the process in kJ/kg k is

1100


HELLO SIR, IAM PREPARING HPCL EXAMS. SO PLS SEND MATERIAL OF HPCL ELECTRICAL ENG..TO VIJAY_8888@YMAIL.COM

1833


When can we take Neutral as common neutral link?

1625


with out colour codeing on conductor how can be find what is r,what is b,what is y phases.....

1913


Refernce currents are to be generated using refernce cueernts how can this be done

2225


Explain the working of any one cutting machine

1062


what will be happen if earth point is being used for as a neutral point for raw power , and same will be used for ups earthing

2047


How do you calculate the actual power consumption of an inductive load appliance. Say, a deep freezer of 200watts

2107


Explain the propagation of harmonics in the network and influence of phase angle of harmonics.

1924


Why do we apply both Differential and REF (HV and LV) protection schemes on YNyn configuration of a transformer?

2105