Which type of DC generator is used for electric welding
purposes and why?
Answer Posted / iamdon
The Differentially compounded DC generator is employed for
welding purposes.The reason is stated as follows.
The Differentially compounded DC generator has very much
drooping characteristic.Thus terminal voltage falls rapidly
with the increase in load current.In welding, the load
resitance is frequently varied by varying arc length.Under such
conditions the value of current should be more or less constant.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 12 Yes | 0 No |
Post New Answer View All Answers
what is KA rating and how can we choose switchgears on applications
why r we using shell transformer for low voltage
How do i perform grounding of star point of Genset (400V) for making connection with step up transformer of DELTA-DELTA (400V to 20KV) ? while Genset itself has its own neutral and grounding bus bar inside genset breaker box whereas we have another neutral and grounding busbar in synchronizing panel next to genset at maximum distance of 6meter, would someone pls advice if we can only perform neutral grounding in synchronizing panel or should we ground neutral on both places inside genset breaker box and synchronizing panel.
Explain Continuous and Discrete signals?
Dear Mr B C pal...Can you plz. put some light on principle of operation of Z-Ct in conjunction to its use with 1Cx1000Sqmm HT Cables & Directional Ground Fault / Over Voltage Relays...Regd..Parag v K 9899115632
How to calculate the input cable rating for 10kva ups (3phase input and single phase output and also 3phase output, battery rating 65Ah)provide the formula also.thnx
what is EIB lighting control system? what is the advantages of this system?
What would cause a 240v choke that should give 110v out on a 16w lamp to gradually increase to 160v?
what is meant by 3rd hormonics ?
What is polar plot?
I need to connect a synchronous generator to the grid using automatic synchronization and two circuit breakers (one for synchronization, one for end connection to the grid), how to determinate the required diameter of the cables?
What is the use of mc( moving coil) in dc voltmeter and dc ammter and what is the use of ( moving iron)in ac voltmeter nd ac ammeter
HOW TO CALCULATE HV TEST VOLTAGE FOR ELECTRICAL EQPT.
please explain to me how to calculate current,voltage,resistance with formula??
5- What is the task (function) of the excitation and isolation transformers in power plant? 6- What is the task (function) of LCI (A), LCI (B) and LCI (COS) in power plant? : LCI (A) and LCI(B) are load commutating inverter for generator turbine starting. , LCI (COS) is load commutating inverter change over switch