Brushed alternator is also called dc generator ? its true
or false ?explain it ?
Answer Posted / lincy
its true,if we are using brushes in alternator it will perform the function of the dc generator that is it will convert the ac voltage developed across the armature to dc and hence does perform the function of dc generator
| Is This Answer Correct ? | 2 Yes | 2 No |
Post New Answer View All Answers
How to select circuit breakers rating eg. if i select a circuit breakers of capacity 40 amps DC with operating voltage 28 volts and if i what to use same circuit breakers for 300 Volts DC application what is the current rating of this circuit breakers.
What is a surge supressor why its is used in synchronous generators
how to calculate voltage drop and followed by cable calculation?is there avail in formula?
what r the checklist while installing a 380 kva DG set
What is the lower limit of break-down voltage of converter transformer.
for 100 HP Induction motor service factor is 1.2(SF) we placed a VFD at the motor side load is balance with 0.3 Amp's Phase to Phase but at incoming of VFD load is un-balance with 10 to 20 Amp's what will be cause of load un balance
what is different between relay and plc?
The screw thread commonly used for transmission of motion is one of the following types of threads
how ups works ? various parts of ups and working principle
What is the current carrying capacity of 35sq.mm flexible cable?
What is the percentage loss for aluminium wire for HT line more than 11KVa
What is limitedly stable system?
How to protect sensitive loads such as Dosing pumps inside a factory from voltage surge/voltage fluctuation.
What are the functions of different probes used in cro?
difference between ac series and parallel circuit