Why in medium voltage system(3.3kv to 33kv, neutral is
earthed with either resistance, reactance or neutral
grounding resistance?
Answer Posted / avdheshlakhera
You need to limit earth fault current in medium voltage
system if rotating machines are connected to the system.By
adding NGR E/F current is limited hence during earth fault
in motors or in generators there will be less core damages.
This will reduce repairing cost of machines (Repairing of
core damages are very costly in large machines). Only thing
you need to do with resistance grounding system is to
select sensetive relays and set them correctly.
| Is This Answer Correct ? | 5 Yes | 2 No |
Post New Answer View All Answers
What are the applications of the electric motors?
i m doing DEEE in part time,can i join regular cources in BE,,IF i join what the cources can i select like (civil,ece,IT) ,,kindly advice
How to check the thermocouple is correctly connected to cable for K type? (i,e positive pole is connected to non magnetic conductor and negative pole is connected to magnetic conductor)
What are m circles?
how we can explain arc heatng?
Sir, plz tell me how droop setting is done in parellel operation od DG set ? please give practical example ?
a)In a 3-phase 4-wire circuit, a circuit breaker is selected to protect the circuit whose highest fault level is 6.6 MVA. Determine the required minimum breaking capacity in kA. (Note: Covert 3-phase power in terms of kA to find answer.) b)Using the below, determine the required minimum making capacity in kA as a “peak value”. Rate breaking capacity (Icn) ka: Icn<= 1.5 Factor = 1.41 1.5
what is the mechanical safety of DG ?
what are the installation procedure of high voltage power transformer,CT,CB&PT?