Answer Posted / sonu kumar

The main advantage of using the star delta starter is
reduction of current during the starting of the
motor.Starting current is reduced to 3-4 times Of current
of Direcr online starting.

Hence the starting current is reduced , the
voltage
drops during the starting of motor in systems are reduced

Is This Answer Correct ?    53 Yes 15 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

in dc series motor if field wdg is shorted then

1445


pls tell what are doing the three phase motor star and delta connetion with circuit diagram and control wiring .

1466


1- What is the Polarization Index number be good for 15KV 3c#500MCM electrical cable? 2- Can I use the IEEE Std 43-2000 to perfom the PI test? Thanks

2917


Is it possible to use a S1 duty class motor for crane application (S4)? If not, why?

1899


why should the primary of transformer be connected in delta in a heat run test?

1472






How can I calculate per unit (KWH) fuel (Gas/ Diesel both) consumption 1MW unit?

1642


How many energy meters can be connected on a 15VA Voltage transformer. please send a calculation sheet.

1512


what will be project cost for 100 kv transformer connection under oyt scheme.

2419


11KV AND 22KV NETWORK KW CAPACITY IN RING AND RADIAL?

1584


EXPLAIN THE TERMS "INTEREST AND DEPRECIATION" AS APPLIED TO ECONOMICS OF POWER GENERATION.

1776


Can anyone provide with a SLD for HT panel installation for a 33KV line and distribution end has three 1.5MV transformers. Is it suitable to use OCB or VCB and also provide me the suitable rating and its connection diagram.

2897


how to select fuse rating for a 3-phase motor ???

1349


how much value of resistance should connect to 15 kw, 6 pole 3 phase slip ring induction motor having RV-240, RA-42.

1460


How to calculate Temp from Resister from PT100 equation,

1210


Why 11kv to be generated in generation station

1258