Can anyone explain in a simple way the difference between
DCS and PLC?
Answer Posted / amzad pathan
These question is very difficult in todays Automation
system, Because Today's PLC is much more upgraded & working
like a DCS. Although PLC is Better for Sequincial
Operation, Because its Scan Time is less than DCS & DCS
mostly used for Continues Process.
If You see todays PLC, Its IO Capacity is near to DCS IO
handling Capasity. Yaa, one Big Advantage of DCS System is
that Logic of whole process is Split in Defferent different
CM's. So that when change in one CM do not affect other
Proccess.
| Is This Answer Correct ? | 15 Yes | 1 No |
Post New Answer View All Answers
Name different parts of a pressure gauge.
Explain PID, ON/OFF, Controls
which processor is used in dcs.
what is the electrical operation procedure for switching on 27.6MVA electric furnace.
protection relay watchdog contact operation?
Why boiler chimney area oxyden sensor fixing?
we are having yokogawa centum cs3000 dcs in our power plant. i need some of the operator guides NOT to appear in HIS0163 AND HIS 0162 but it shoul appear in HIS0164 HOW TO DO IT?
steps for installing orifice plate?
What is eddy current? Describe the operating principle of proximity probe.
Which is your favourite subject & explain any one topic of it.
What is loop1 and loop2 in MTS LT?
find the kp ki kd from the transper function G(S)=29.44s+04707/1.5349s2+s
I am having a Phoenix digital to modbus converter. The o/p of the same is connected to flow computer FB407. But the digital signals are updated only after one minute in the flow computer. what may be the cause of delay in communication? Flow computer is having a scanning period of less than 1 sec.
What is mean by analytical instrumentation?
Isometric drawings are generated during _________________ phase of a project