The principle involved in working of a transformer is
mutual induction. Both electrical and magnetic energy are
interchangeable.
Simply saying change in magnetic field creates emf.
i.e., if flux linking with a coil changes due to the
current flowing in the same coil, then the type of emf
induced is called self induce emf.
Similarly if the flux linking with the coil is changing due
to the current flowing in another coil, then the type of
emf induced is called mutually induce emf. This is the
principle involved in transformer.
The transformer has two windings namely low voltage (L.V)
and high voltage (H.V). These two coils (windings)
magnetically coupled but electrically isolated. The
connection between these two coils existing when there is a
change in flux which is only set up by AC. This is not the
case in that of DC.
Dc means no change in flux-> no emf -> no coupling between
two coils.
So the winding which we give supply is just seems to be
short circuited. So if the resistance is not capable to
oppose the current-> high current-> coil burns.
What will happen if I apply DC to AC transformer?
Theoretically not works
But practically the transformer will burn. It may be
varying for rating of the transformer also.
Transformer means it is for ac only
No need to say it as ac transformer.
| Is This Answer Correct ? | 9 Yes | 2 No |
Post New Answer View All Answers
Explain the advantages and disadvantages of thermal power plant?
why connecting surge unit in contactor coil
what is the use of surge suppresser in 33 KV incoming panel. where it must be installed,inseries with incoming cable surge suppresser must be at incoming of the breaker are outgoing of the breaker
i need of the bhel question papers along with answers and also give some website names for the downloading question (electrical and electronics engg question)please help me....
What is the difference between single point and double point bonding. please kindly detail about bonding of cables.
how calculated Transformer losses.
What happens if the Capacitive Voltage Transformer Primary neutral is not earthed. There is a CVT between Transformer and source, and the CVT neutral of the transformer is not earthed, does it effect the transformer while charging or does it effect the transformer charging process.
What is knee point voltage of transformer?
What is the disadventage of gland earthing(power cable) if any. ?
Draw a block diagramof Three UPS systems connected in Parallel mode?
What is the difference between acs 550 & acs 850
We need to current density & short circuit calculation at 65kA for aluminium & copper busbar.
If anyone would like to know or practice for FEWA papers contact me on mohamedrashad2@hotmail.com Just completed the supervisor exam in April 2021
What is the different between digital phase converter and ordinary phase converter?
suri transmission