Why the Potential transformer Primary in connected to Earth?
Answer Posted / koodalingam
To protect the primary winding of the potential
transformer.If you not earthed the system,the unbalance
voltage will appear between neutral and earth.This voltage
can damage winding.
| Is This Answer Correct ? | 10 Yes | 1 No |