how winding temperature detects in power transformer...?
Answer Posted / ullas
a special CT(current transformer ) is used to measure the
winding temperature in a power transformer.
the method is very simple, there will be one winding
temperature measurement pocket in the transformer. in this
a temperature measurement device is dipped and this pocket
will be filled with transformer oil. this special CT will
give output in the form of current which is proportional to
the temperature.
i think this makes a clear picture.
| Is This Answer Correct ? | 23 Yes | 5 No |
Post New Answer View All Answers
how to handle 2500 kva transformar
Which thing is maximum in RLC circuit at resonance a)power consumption b)inductive current c)capacitive voltage
What is electrical grounding?
What is the rating of circuit breaker needed for 300 KVA load in 33 KV supply line in a transformer of 33 KV / 415 Volt ?
10 Mtr Hight of Lighting Arrestar how much area coverd??
What is meant by celling voltage & current in excitor ?
why 1.7Uo for HV cable Hi pot test?IE standard why?
1- XC and the RC time constant are both measures of the reaction of C to a change in ____? 2-The power factor is a numerical ratio with a value between 0 and 1 equal to the ______________ of the phase angle. 3-When V and I are out of phase because of reactance, the product of V times I is called ______________ power 4-For _____________ inductors, the branch currents can be added algebraically. 5- The ______________ power in watts can be calculated as I^2R 6-Calculate XL with L = 30mH and f = 1kHz ( I have Xl=2piFL 2*3.141592653*1kHz*30mH =188 ohms Please check) 7-A parallel RL circuit has the values, R = 5kohms, XL = 5kohms. A voltage source of Vt = 10Vrms is connected in parallel to R and L. Determine the total current, It delivered by the voltage source Vt. 8-A series RC circuit has R = 1Mohm and C = 1microF. How long would it take for the capacitor to fully discharge if it is initially fully charged? 9-A circuit has real power = 300W and an apparent power of 500VA. Determine the power factor and phase angle. 10-The time constant for an LR series circuit is T = 0.1s and R = 10ohms. Calculate the inductance L.
Define super node?
What are IR values and what it should be for coil and for insulator
How to synchronization will be done between two DGs ?
HOE WE CAN IMPROOVE BY USE OF CAPACITOR
How to size Air Circuit breaker (ACB)? What is the most important factors?
HOW CAN WE DECIDE THE SUPPLY VOLTAGE FOR MOTOR ACCORDING TO ITS RATING(IF ANYONE KNOWS GIVE IT WITH EXAMPLE AND ITS CALCULATIONS)
What will happend if given Vfd out put to step up transformer