AC current is flowing in a wire in your home how can you
measure it(name of the instrument)
Answer Posted / gkumar
Hi,
If u want to test the line u can use line tester
if u want to measure the total current of ur house u can use
clamp on meter
If u want to measure current for a particular equipment u
can use multimeter ,ammeter ,tong tester/ clamp on meter.
And if u want to test a three phase line continuity u can
use two lamp connected in series of same wattage.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
How to decide no. of Step and Kvar for APFC Panel 40 kvar MD: 33.12 KVA Avg pf : 0.8540
describe the A.C. Generator Testing procedure
What do you mean by dependent and independent voltage sources?
Power factor =1.000 at factory in supply. However, PF = 0.8 at motor end. Current = 100 Amp, Voltage = 400 V. What is the power distribution loss? Can I reduce it by adding capacitor at the load feeder?
Which type of questions well asked. ?
what is formula for zero phase sequence of nuetal earthing transformer of 6.6 kv
what is the minimum voltage require to injure our body?
how to calculate distance between busbar supporters for LT panel, what are the factors influencing in this design
What are chief characteristics of state-space method and its techniques ?
can a 150 kva 3 phase 440v/230V delta-wye step down transformer can be use as step up transfoermer with connected loads at 440v side?
What is the formula of frequency ?
Why do we use center tap transformer that used with portable tools
placing earthing pit in pathway is correct or wrong??. placing earthing wireGI1/18 inside walls is correct or wrong?. explain!!!
when it is possible kvrah lead & fundamental kwh be equal in electonic trivector meters (3 ph)
How to work E.L.C.B and how to connect in circuit.