How can i calculate knee point voltage of 800/5A Current
transformer?please explain me with suitable calculation?
Answer Posted / gunasekaran
1.2*VA*ALF/rated secondary current
suppose the ct is 5P20 class and 20VA burden we can
calculate the knee point as follows
1.2*20*20/5=96V
| Is This Answer Correct ? | 9 Yes | 6 No |
Post New Answer View All Answers
What are the relays in ACB and VCB
What are IR values and what it should be for coil and for insulator
What is Control & Relay Panel? And Remote Control Center?
Difference between low impedance and high impedance Restricted Earth Fault
Whether should be the oil level in OCTC transfomer? It should be upto winding immersed completely or should be upto tap changer s/w? How it will affect the performance of the transformer. Rating may be 33KVA
could you measure current in parallel?
Earth bits close or open. Which is correct
Electrical 'C' license full abbreviation , and full form
3ph motor running with unequal kw and different pf what are the reasons
Enlists the applications of sampled data systems?
is there any role of power factor with frequency variation? and how we can manage the frequency variation?
can u give me a brief idea about power line carrier communication ??
What is current & voltage ? Voltage perform at any load without current or not?
why does make gain margin and phase margin on same plot.?
I want to know all basics of electrical engineering