How can i calculate knee point voltage of 800/5A Current
transformer?please explain me with suitable calculation?
Answer Posted / gunasekaran
1.2*VA*ALF/rated secondary current
suppose the ct is 5P20 class and 20VA burden we can
calculate the knee point as follows
1.2*20*20/5=96V