the voltage per turn of a primary winding of a transformer
is the same as the voltage per turn of the secondary
winding of the transformer. why?
Answer Posted / saranya
E2/E1=N2/N1(Voltage transformation ratio)
E2/N2=E2/N1.so the emf per turn is same.
| Is This Answer Correct ? | 10 Yes | 5 No |
Post New Answer View All Answers
what are the pecularity of shaver sockets ?
how open delta PT works & what is its construction?
what can be the causes of capacitor start motor having a higher current that its actual
design a 3 bit synchronous and asynchronous counter using T- flipflop
what is the internal working of star delta starter
How are load losses and no-load losses measured at site in a DG set?
What is transient response?
primery try cell?
What are m circles?
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
(1)Can earth and be conected together (2) what is the diferent between earth & neutral
what is the Connected Load (kW) or Contract Demand (kVA)of mahindra nasik plant??
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
WHY THE DIMENSION OF TWO SAME RATED MACHINE IS DIFFERENT ?
How we can calculate the life of Lead acid battery