what is the difference between KVAR & KVA ?
Answer Posted / shriram gaur
KVA=V*I
this is used for measureing the total power fed into the
ckt, so generally used in defining the rating of the
transformer, also independent of PF.
KVAR - sqrt((KVA*KVA)-(KW*KW))
This is the correct relationship between the all three
power.
| Is This Answer Correct ? | 7 Yes | 13 No |
Post New Answer View All Answers
how can i get the formula to find out the cable size if i know the load of main fuse protection.
What is the difference between isolators and electrical circuit breakers?
defination of lines
100 MVA 3-phase alternator with earthed neutral has a reactance of 5 ohms per phase. what will be the fault MVA of generator.
What are the necessary components of the feedback control system?
Why does the speed regulating system adopting I controller have no steady-state error? In this single closed-loop speed regulating system, when the input of the I controller Un=0, what is the output voltage of the regulator? What factors do the output voltage depend on?
Explain Even and Odd signals?
Can the output voltage of a rectifier be greater than the input AC voltage without the use of any voltage multiplier in the circuit??please provide the explanation too..
HOW MANY TYPES OF FUSE?
Which do you think is the most significant cause of energy loss in a factory?
how single phase preventer works ?
how is the incoming cable size calculated for a given current rating of a panel??
how to test YNyn0 vector group in transformer?
How to arrange a hous hold earthing system to keep minimum earth resistance( below 7ohms).
in single phase converter, the no.of scr's conducting during overlap a)1 b)2 c)3 d)4