i want to Measure the Difference pressure of Packed distillation Column of height 3 mtr. h.p. side connected to
bottom & L.P. side connected to the top , so tell me what
will be THE URV & LRV of that D.P. transmitter?
Answer Posted / sateesh kumar singh
If you want to mesure a differential pressure of Packed
distillation Column and currect out put signal then
instrument mesuring rang should be higher than required
measuring renge.
URV >3000 mmm WC ( Say 4000 mm WC)
LRV= 0 mm WC
calibrate it 0 mm WC to 4000 mm WC .
| Is This Answer Correct ? | 0 Yes | 3 No |
Post New Answer View All Answers
What are the different types of thermistors used in industries? How to the operation of typical thermistor?
Instrument QA/Qc what is the project quality plan?conduit inspection RFI. which documents attache with package?
how do i tune dearator pr control valve using PID. we set the set point is 0.6kg/cm2 now i want 0.5 to 0.7kg/cm2 limits so what should i give p,i,d values. then pls explain how do set pid values for control valve tuning?
Coal mill Instruments Equipments for cement plant And process diagram ?
Explain the key components of control loop?
can any send me a forbes marshall dtron 316 manual
Draw a great bridge circuit.
Explain about safety integrated level protection? . How it was differ from other protections ?
what is o2 analyzer and how it measured ,what is the role of this analyzer in cfbc boiler...
Specific gravity.
the 3 most common transmitter protocol being in refinery or qatar gas and aramco.
what is the difference between active & reactive power?
What is Droop? What is Step/Gradient Limiter in Turbine Governor control?
What is difference of fanuc alpha series 16i and 18i controller.also what is differnce betn TC and MC controller
What are different types of cable?